03-02-2011, 12:50 PM
hello I am trying to find information anywhere to the size of BPHE to use for condensor and evaporator for a ground source heat pump also the water flow and length of loop, I was going have a 5hp scroll to use and I was told that is comparable to 50,000 btu which would heat this house adequately any ideas would be appreciated or tell me to go to ref 101, which i did read
thanks ed,
Bigfreeze
03-02-2011, 08:20 PM
hello I am trying to find information anywhere to the size of BPHE to use for condensor and evaporator for a ground source heat pump also the water flow and length of loop, I was going have a 5hp scroll to use and I was told that is comparable to 50,000 btu which would heat this house adequately any ideas would be appreciated or tell me to go to ref 101, which i did read
thanks ed,
The SWEP website should have the information you are looking for. Look under the Nordic heat exchanger section
nike123
03-02-2011, 10:36 PM
For R407C:
Evaporator capacity would be around 11 kW and condenser capacity would be around 15 kW.
What would be as heating element, fan-coils or underfloor heating?
What refrigerant is used?
http://i51.tinypic.com/20krabl.jpg
http://i56.tinypic.com/axeefp.jpg