View Full Version : daikin split cycle airconditioner model rxd71Jvea



hudsonhawke
02-02-2011, 07:14 AM
I have just been advised by a tech that the code presented on this unit has a code H27? in short the compressor is dead. He suggested I buy another split air conditioner as it wasn't worth repairing. Is the tech right with his diagnosis or can I replace the compressor. This unit is 10 years old and only used been usedon extreme temperature days . The compressor died on a day the temperature was 38-40 degrees celcius.:confused:

superswill
02-02-2011, 08:04 AM
theres a few factors to consider here,

if the system is ten years+ parts may be difficult to source

what refrigerant the old system is, will it be replaced with a more energy efficient so running cost can be lower that can be offset against new install.g from R22 to R410A will be more energy efficient

is this the first of many problems to come

also if the system is in the UK there also UK F gas regs to take into account if the system is R22

install monkey
02-02-2011, 10:37 PM
h27 isnt a daikin fault code.
check the compressor hasnt overheated and cut out on internal klixon

install monkey
02-02-2011, 10:48 PM
00 OR ∗ Indoor unit in normal condition (Conduct a diagnosis of the outdoor unit.) —

A1 Inverter unit - Faulty indoor unit PCB 89

A5 Operation halt due to the freeze protection function or high pressure
control
90

A6 Faulty fan motor (DC motor stop) DC motor 91

A6 Faulty fan motor (AC motor stop) AC motor 93

C4 Heat exchanger temperature thermistor or related abnormality 94

C9 Suction air thermistor or related abnormality 94

CA Discharge air thermistor or related abnormality 94

∗ Faulty indoor unit PCB 95
96

∗ OR U4 Faulty power supply or indoor unit PCB 97

U4 Signal transmission error (between indoor and outdoor units) 98

UA Faulty indoor / outdoor power supply specification 99

∗ OR E8 Operation halt due to detection of input overcurrent 106

E5 Stoppage by OL actuation/Melt-down by temperature fuse 102

E6 Opeartion halt due to compressor seizing 104

E7 DC fan motor seizing 105

F3 Abnormal discharge pipe temperature 101

H6 Operation halt due to faulty position detection sensor 108

H8 Operation halt due to detection of CT abnormality 109

H9 Operation halt due to outside air thermistor abnormality 112

J3 Operation halt due to discharge pipe thermistor abnormality, or due to
detection of disconnected discharge pipe thermistor
112

J6 Operation halt due to outdoor unit heat exchanger thermistor abnormality 112

L5 Operation halt due to detection of output overcurrent 110

U0 Operation halt due to detection of insufficient gas 113
U2 Main circuit overvoltage or low voltage 115

install monkey
02-02-2011, 11:23 PM
H27 �� �� �� protective device for compressor is activated, compressor no. 2 oil sensor fault (disconnection,
sanyo???

install monkey
02-02-2011, 11:25 PM
H27 Off Off Off Off Outdoor Air Sensor Faulty Sensor Disconnected, Faulty or Contacts Dirty
panasonic?

paul_h
03-02-2011, 10:32 AM
Daikin fault codes are 2 characters, not 3, so it can't be H27, could be H7 for example.
The JVEA units aren't very good, parts are expensive, so I'd buy a new unit instead of repairing myself.