View Full Version : Roca York BRAW-150-1-38B water chiller



coolflow
01-02-2011, 11:05 PM
Hi any one got the fault codes or any help on this. it has a Microtech controler that has E03 code just after start up.And as you all know the tight custmer dose not want to replace the system even tho its 15 yearss old..!! :mad:

Grizzly
01-02-2011, 11:38 PM
Alarm E03 from a later microtech. It may be a help?
Grizzly


Thermal switch protection compressor 1


Compressor 1 will be shut down;
Triggered by the digital input configured as "Thermal switch compressor 1" (refer to digital inputs);
Automatically reset until alarm events per hour reaches the value of parameter Pa A07, after which manually reset;
Inactive during timer Pa A08 after compressor on.

coolflow
02-02-2011, 07:26 AM
Thanks, well er yes,ish, so it could be the comp sensor ? any pdf of this unit avalible or bypass tricks,or paperwork avalible online?

NoNickName
02-02-2011, 07:32 AM
Maybe the sensor is not faulty and the compressor is kaboom.