View Full Version : undercharged?
Welder
30-01-2011, 11:32 AM
Newbie!!
Got a low discharge temp on compressor 48c icing back on suction.......undercharged?
sedgy
30-01-2011, 12:02 PM
hi welder , have you got clean filters ? is the evap fan running < full revs<? sedgy ,
marc5180
30-01-2011, 02:08 PM
Newbie!!
Got a low discharge temp on compressor 48c icing back on suction.......undercharged?
A lot more information is needed to know if it is undercharged such as;
What is the superheat?
What is the subcooling? ( if applicable)
What type of expansion device? Fixed or tev?
Air on/off indoor unit
Air off outdoor unit etc etc
charlie patt
30-01-2011, 03:42 PM
if iceing suction heavily its overcharged or if it has a tev its bypassing is the coil iceing when the suction pipe is? more ifo required ie temps tev or cap type of machine superheat as above really
Brian_UK
30-01-2011, 07:32 PM
Welder, as Marc says, you really must start giving a few more facts if you want a decent answer.
It's a bit like me saying that I have a 36" waist, what colour are my eyes and why?
One single reading and a quick look do not a diagnosis make.
You've got 48°, is that air temperature, the temperature of your gas torch cooling down or your coffee from Costa's?
tonyelian
30-01-2011, 07:32 PM
hi
if you meant an air condition system its under charge but if it is a refrigeration system more info more help