I've just intalled a city multi at a store, one outdoor,4 cassetse,and one controller.
the question i have is there any way of locking the temp set point on the controller to stop the staff at the store from messing about with it:mad:
Any help much appreciated
mant thanks.
install monkey
29-01-2011, 09:35 AM
on a par21 The following settings can be made.
no1 :All buttons except for the [ON/OFF] button are locked.
no2 :All buttons are locked.
OFF (default) :No buttons are locked.
* To activate this operation lock function on the normal screen, hold down the ON/OFF button for two seconds while
holding down the FILTER ( ) button
marc5180
29-01-2011, 09:39 AM
Or if you have a Par 27 to lock all the buttons other then the on/off button,
Press the [on/off] button for 2 seconds whilst holding down the [FILTER] button.
Alternatively you could also set a temperature range limit on the controller.
install monkey
29-01-2011, 09:42 AM
temperature limit settings are
(1) While pressing the MODE button, press the ON/OFF button for two seconds to activate the remote controller’s
function selection mode.
(2) Press the MODE button to select FUNCTION
SELECTION on the screen (at ).
[Display ]
(3) Press the MENU button to select LIMIT TEMP
FUNCTION on the screen (at ).
* If a setting change was made previously, the mode that was set (one of the modes shown in step (4)) will be displayed.
(4) Press the ON/OFF button to select the mode for which temperature range limit setting is to be made.
[Display ]
* No operation modes will be displayed if auto mode has been set to OFF
Press the button to select lower limit or upper limit.
Lower limit blinks. Upper limit blinks.
[Display ]
(6) Press the [TEMP] buttons ( and ) to set the desired temperature setting range.
[Setting example for lower limit]
(7) While pressing the MODE button, press the ON/OFF button for two seconds to return to normal mode. Setting is
now complete.
* If you press the ON/OFF button before the MODE button, the settings you have made will be cancelled.
* If an attempt is made to set a temperature outside the range when the temperature range limit function is in use, “LIMIT
TEMP FUNCTION” will blink.