charlie patt
28-01-2011, 08:29 PM
looked at a 550 carier 1993 model on r22 no heating found hg valve coil faulty replaced found not charging all sorted but it now brings up sa sensor supply air i pressume but i thought supply air sensors where only on units with extra heaters which this unit has not display on controller reads what temp is any advise ta charlie;)

abbsnowman
29-01-2011, 03:53 AM
That does sound odd. I wonder if the micro is configged wrong? Do you have a book? If not, post your email and I will send you one that should be close. (Our units are slightly differant.)
Abbs

charlie patt
29-01-2011, 05:45 PM
ta will do i am also wondering if there is another fault as ra sensor works ok and its shutting down on another fault?

abbsnowman
30-01-2011, 12:34 AM
I'm not sure about over there but over here that unit does not use supply air sensor. I would expect to see an "RA" sensor but now an "SA"

charlie patt
30-01-2011, 10:03 AM
have found ra sensor and that brings up ra fault but sa only used to be for seperate heater bank which it doees not have any advise

abbsnowman
30-01-2011, 06:34 PM
You will need to get into the configs and chack them. Start there. Best way is to use a laptop. You can also jump the serial port but I don't like seing people do that unless they know what they are doing.

charlie patt
30-01-2011, 07:26 PM
whats the serial port route then please advise

abbsnowman
01-02-2011, 05:03 AM
First I need to know your knowlage base. I don't want to be reponsable for you nuking a micro. Do you have a config list?
I will help you but I don't think I will be helping you if I put you beyond your capability.
Do you have a manual?

charlie patt
01-02-2011, 08:26 AM
out of touch on these old units have the laptop for the new units but it wont let me in yhese no manual either