PDA

View Full Version : Freezer/Cooler Question



mrgbfan
27-08-2005, 12:01 AM
I am not an engineer, but I do own an industrial novelty display type freezer. It is a Masterbilt GT40. I need to know if it would be OK for me to change the thermostat in the unit and convert it to a cooler? I was warned that this may shorten the life of the compressor due to 'short cycling' it.

Jus Walker
27-08-2005, 07:01 PM
It does depend on the gas.
Because when it is used as a freezer, the gas will be coming back to the compressor to help cool down the head. So it might not be a good idea. Try and find out what the gas is. I think it will be on R404a.

mrgbfan
30-08-2005, 12:12 AM
Yes. The spec sheet says it is R404a:confused: .

Kevin Yeo
04-09-2005, 03:50 AM
If it is R404a gas, then it will have sufficient ref mass flow to cool compressor head. However, is the condenser sufficiently large enough to cater for mid temp capacity?

May need to monitor high side pressure...