So.......got this Super Yacht that we are carrying out repairs on.
The current set up as follows.
Freezer room and coolroom have exactly the same components, with the orifice the only difference. R404a
Evap - ECO200ED - rated at aprrox 1 - 1.2 kw ish?
Danfoss TES2 TX - CR Orifice #4 6.08kw , FR Orifice #6 7.78kw.
Compressor DWM Copeland DKSJP-15X rated at 3.8kw medium and 1.6 kw low.
Given the complete inbalance of the systems, you'd think they wouldn't work, But yet they do, and quite well too. Aaaah the intricacies of refrigeration!
The current set up as follows.
Freezer room and coolroom have exactly the same components, with the orifice the only difference. R404a
Evap - ECO200ED - rated at aprrox 1 - 1.2 kw ish?
Danfoss TES2 TX - CR Orifice #4 6.08kw , FR Orifice #6 7.78kw.
Compressor DWM Copeland DKSJP-15X rated at 3.8kw medium and 1.6 kw low.
Given the complete inbalance of the systems, you'd think they wouldn't work, But yet they do, and quite well too. Aaaah the intricacies of refrigeration!