i have a fujitsu ASTA09JCC indoor unit with active codes.
the red and green LED's flash together twice then the red LED will flash on its own foiur more times.

please help

7258james
02-02-2011, 12:01 PM
Hi There, In regard to your fault code it doesnt sound familiar. Two lights flash then four times? Are you sure thats right? I have all the fault code listings for Fujitsu in regard to inverters and not one matches up..four flashes is a PFC fault which is the power factor controller which regulates the power in the circuit which is part of the main controller board in the outdoor unit. Have you got the Red LED on the outdoor unit on/flashing?

7258james
02-02-2011, 12:07 PM
Also If the Red operation light flashes four times you could be looking at an indoor unit power interruption...But i need more info to be more certain cheers mate

Sserrviceman
02-02-2011, 03:13 PM
Maybe Timer (Green) - 2 times blink
and Operation (Red) - 6 times blink.
It is - indoor fan motor lock error.
Some info from Fujitsu. Look p.02-02 and p.02-14 here: http://www.goductless.com/v/vspfiles/assets/images/pdf/fujitsu/dual%20zone/asu9rmlq_service.pdf

superswill
02-02-2011, 05:08 PM
see attached, not sure if it is relevant to your model

emjay
03-02-2011, 11:26 AM
according to fujitsu error contents, 6 red + 2 green flashes indicates indoor fan motor, abnormal lock.

gavin g
03-02-2011, 11:56 PM
according to fujitsu error contents, 6 red + 2 green flashes indicates indoor fan motor, abnormal lock.
hi, yes you are right!
the indoor fan is U/S
Thanks heaps for the help.