View Full Version : Toshiba RAV series L29 fault??



Alan.D
24-01-2011, 11:02 PM
I was called to a site with a unit showing this fault, reset unit and ran away fine for about 5 hours, cut out on same fault. Toshiba tech support wasnt in the office so he couldn't help. I checked a few other units in the building and they showed the same fault in the memory. Can anyone help?

Thanks

install monkey
24-01-2011, 11:11 PM
L29 Error on outdoor unit, etc.
· Communication error between
CDB and IPDU
(Coming-off of connector)
· Heat sink temperature
error
(Temperature over specified
value was detected.)

1. CDB and IPDU wiring cables check
2. Abnormal overload operation of refrigerating cycle

marc5180
24-01-2011, 11:13 PM
Error on outdoor unit, etc.
· Communication error between
CDB and IPDU
(Coming-off of connector)
· Heat sink temperature
error
(Temperature over specified
value was detected.)

1. CDB and IPDU wiring cables check
2. Abnormal overload operation of refrigerating
cycle

marc5180
24-01-2011, 11:14 PM
Install Monkey you beat me to it :D

install monkey
24-01-2011, 11:15 PM
mark5180 beat by 2 mins haha-we must have the same library of manuals

marc5180
24-01-2011, 11:16 PM
It looks that way doesn't it ;)

Alan.D
24-01-2011, 11:39 PM
Ambint temp where condensers are located is about 40 Celsius so over temp of heat sink sounds to be right. I'll check all the other possibilities too. That fact that other units have had same fault is a clue too. Thanks for you help guys

install monkey
24-01-2011, 11:53 PM
check the condenser coils are clean and put some systems in heating to lower the ambient around condensers,also ensure the inverter cooling fins are clean too