View Full Version : upside down fridge/freezer not cooling properly


Barney01
23-08-2005, 05:29 AM
Hi,

I have recently bought a second hand 420 litre frost free westinghouse with the freezer on the bottom. It is about 3 - 4 years old.

Its been plugged in for about 3 days now, and the freezer section is not that cold. I have both the fridge and freezer thermostats on coldest, and neither section feels as cold as it should be. The fan has been running continuosly - it seems as if the fridge isn't cooling for whatever reason so the thermostat tells the compressor to keep running. The fan will turn off if I twist the thermostat around to warm.

Any ideas greatly appreciated.

aircon
23-08-2005, 11:54 AM
Take out gas weigh and recharge may resolve problem.

slingblade
29-09-2005, 03:11 PM
question? what is the refrigerant? what is the suction pressure? what is the air td over the freezer evap? if its a fan assisted condensor, what is the ait td over this?

chemi-cool
29-09-2005, 08:02 PM
Hi Barney01,

Are there two compressors?

If it runs on 134, It is in many cases, a blocked cap tube.

Chemi:)

chillin out
29-09-2005, 09:54 PM
Erm guys,

I think barney01 came here posted that and aint been back since which was a month ago.
:) :)

Bones
07-10-2005, 08:20 AM
should be a single comp job running on 134a