Hi.
Looking for some advice. Have a compressor failure ( L'unite Hermetique CAJ2432z) on a foster single door freezer. Customer has a compressor ( CAJ2446z) on site. Same pipe sizes and physical size. New compressor is 1/8hp more powerful than existing. Is it possible to install this more powerful compressor?
Thanks.

Brian_UK
20-01-2011, 11:15 PM
CAJ2446 has 43% more duty capability than your original.

Do you have fanned compressor cooling on this model?

Serge1204
20-01-2011, 11:19 PM
It's not a fan cooled compressor, brian. Would this make a difference?

Brian_UK
21-01-2011, 08:09 PM
It's not a fan cooled compressor, brian. Would this make a difference?
They are according to the manufacturers.

install monkey
21-01-2011, 08:55 PM
normally compressor replacement is based on displacement,type of expansion device. and application -low back pressure for freezers,medium for fridges
caj2432 18.3cm3 displacement 5/8 hp
caj2446 26.15cm3 displacement 3/4hp
low back pressure high start torque.