I have one suggestion in Toshiba VRV System
1.Why Liquid line sweating?
2. No Cooling in room
Compressor Discharge line temp-92.6c
Compressor suction line temp-20.5c
Liquid line Pressure-285psi
Suction line Pressure-80psi

I am expecting positive Feed back from your side ..........

Loops
20-01-2011, 11:45 AM
Hi There,

Model numbers of the outdoor unit \ indoor units and how many indoor units would be useful.

Which refrigerant is this VRF using?

Cheers

Loops

Tayters
20-01-2011, 08:37 PM
Sweaty liquid line and high(ish) compressor discharge temperature indicate short of refrigerant.

Andy.