14-01-2011, 10:31 AM
Hi all has anyone seen oil migration on a Xarios 350 when operating in standby mode?
We have lost two standby compressors,:eek: we removed both the standby comp - no oil and the road comp which was over flowing with oil. We have checked the TX valve for flooding etc.
The normal set point for this unit is - 25 as it carries ice cream.

radekklimat
14-01-2011, 05:10 PM
Replace with a new oil separator

charlie patt
14-01-2011, 05:46 PM
oil sep when you drain it it will be full of debris

thermo690
15-01-2011, 06:37 AM
We replaced the oil sep between the two comps :(

climas
15-01-2011, 09:34 AM
Common problem when unit works in that aplication,small Te small refrigerant velocity and bad oil return.
Check Te and superheat when unit works near set point.
Nightmare in any case

Satukyza
20-01-2011, 05:41 PM
Solve the problem by installing the oil return kit ref: 76-61254-00.

pechilly
31-01-2011, 03:35 AM
Had this problem, found that the Sby comp check Vv had an intermittant fault (pig of a thing to find)

thermo690
31-01-2011, 09:32 AM
Had this problem, found that the Sby comp check Vv had an intermittant fault (pig of a thing to find)

Same here a right pig and cost was high:eek: