View Full Version : Copeland 20HP compressor D4ST-200X



ktmtragic
13-01-2011, 07:02 AM
Still working on this quote for a customer and price seems to be the ONLY consideration. The maximum running current is stated at 45Amps. so I am thinking I will have to use an 80 amp circuit breaker. I was wondering with the part winding start if I could drop it to a 63 Amp D curve breaker. The reason is of course the difference in cable sizes your thoughts would be appreciated

Magoo
13-01-2011, 10:47 PM
The more bits you add on and multi cable runs, twin contactors and overloads, delay timer etc., the higher the install costs. Base the D curve breaker on LRA rating and overloads on FLA. Add and unloader head if power supply is a problem