View Full Version : Suction values jumpin around



stanthonycold
12-01-2011, 07:26 PM
Hi,

Sabroe 163 mk compressor.the suction pressure and seq. suction pressure values are all over the place .Jumpin from for example 2 hg to 2 psi .Just changed tranducers cable and sensors but still happening .Anyone have an idea on what could be going on here ?

Terron
12-01-2011, 07:38 PM
So far you have; Checked sensor location for oil, calibrated sensor and even installed a gauge beside it, replaced sensor and cable....and you are still getting problems. Did you zero out your Static offset? For example if you installed a 0 to 150# transducer.....input 0 for min and 150 for max?

stanthonycold
12-01-2011, 07:52 PM
So far you have; Checked sensor location for oil, calibrated sensor and even installed a gauge beside it, replaced sensor and cable....and you are still getting problems. Did you zero out your Static offset? For example if you installed a 0 to 150# transducer.....input 0 for min and 150 for max?

Yes i have none all of that ,cant understand whats going on here !

TXiceman
12-01-2011, 07:58 PM
Has the transducer always done this or is it something new?

Whet is the sensor located relative tot he sensing point?

have you tried to throttle the block valve to the sensor?

Have you confirmed the readings with a gauge ?

It may be an electrically induced change and not mechanical. Is the cable properly grounded?

It may be a problem with the point on the control board.

Terron
12-01-2011, 08:25 PM
You did change like for like, for instance if it was a 1-6 volt transducer you replaced with 1-6 volt, not a 4 to 20 milli amp. and you said you did replace the wire so there couldn't be any rubbing issues there....And you positive you wired it up right? There really isn't anything trick about them. Is it coming off a three way valve? When did this problem occur? Have you had any electrical issues, (ie lightning storms)?

Terron
12-01-2011, 08:28 PM
Who designed your control system?

stanthonycold
12-01-2011, 08:29 PM
Has the transducer always done this or is it something new? yes but not so bad ,thats why we chnaged it out cuz we thought it was the trouble

Whet is the sensor located relative tot he sensing point? on top of lpr

have you tried to throttle the block valve to the sensor? YES

Have you confirmed the readings with a gauge ? YES the gauge readings are right on

It may be an electrically induced change and not mechanical. Is the cable properly grounded? YES I think electrically induced as well

It may be a problem with the point on the control board. NOT sure.Cant seem to figure it out ,had a the electrician look at it and he said it could be electronic noise but we dont think thats it but could be

TXiceman
12-01-2011, 09:28 PM
Put a mechanical gauge on it and see if it follows the transducer..pretty simple. If the guage is steady, them it is a problem with the electronics.

Ken

stanthonycold
12-01-2011, 09:32 PM
Who designed your control system?
M&M refrigeration

Terron
12-01-2011, 09:38 PM
That's what I thought, I will send you a contact number for M&M. He will be able to pin point a problem.

Grizzly
12-01-2011, 09:58 PM
Can someone tell me.
Do M&M supply their own control software and Hardware or do they use the Sabroe Unisab Control system?

Hi Stanthony.
Is your pressure transducer a Danfoss AKS 32R as is supplied here in Europe.

I may be able to help but because of size details I will have to email them to you, rather than post them.

It's relatively easy to test the Signal / voltages from them.
Grizzly

stanthonycold
13-01-2011, 02:41 PM
Can someone tell me.
Do M&M supply their own control software and Hardware or do they use the Sabroe Unisab Control system?

Hi Stanthony.
Is your pressure transducer a Danfoss AKS 32R as is supplied here in Europe.

I may be able to help but because of size details I will have to email them to you, rather than post them.

It's relatively easy to test the Signal / voltages from them.
Grizzly

Gauge pressure for seq. suction and compressor suction gauge reading are pretty much dead on when in sequenced mode.M&M is telling us to keep in sequenced mode while we r using just 1 compressor but i always figured you use seq mode when running 2 compressors .

Terron
13-01-2011, 03:07 PM
Seq. mode removes each compressors micro panel reading and replaces it with the house reading. So they will all be reading the same suction pressures when staging on and off. Did you get the number I sent you?

Terron
13-01-2011, 03:08 PM
So yes, you would tend to use it when running multiple compressors or a trim compressor.

Terron
17-01-2011, 03:55 PM
Have you come any closer to solving your problem?

unires
28-01-2011, 09:35 AM
Chanche o rink in safety valve on comprecor