Jase
09-01-2011, 10:32 AM
1) Outdoor : PURY - EP300YHM-A
2) BC Controller : CMB -P108V-GA
3) 7 x fan coils
4) AG 150 Centralised controller
Been having problems with commissioning the above system.
Experiencing voltage drops on the M-Net transmission.
Reading 29.4 Vdc @ the M-Net board on outdoor unit but upon testing voltage inside at fan coils the reading drops to around 25 Vdc.
It's not a long cable run. Have even replaced the cable but not much joy. Prior to changing out the cable there was 2 fan coils with no LED's showing on the PCB's. Also no LED at the BC box. Checked power supplies and found all to be satisfactory. Power being supplied from transformers to PCB's too!
Once the cable was replaced the LED's for the fan coils came on but still no LED on the BC box.
The AG 150 is not showing much too. It shows the address settings of the fan coils and local remote controllers and is in alarm condition. Fault is '6607'.
The control for this system is being used on the M-Net set up. The remote controllers are wired in on the M-Net transmission.
There are only 4 x remote controllers being used and all system is addressed.
Address:
unit 1 - 001 no remote controller
unit 2 - 002 remote controller - 102
unit 3 - 003 remote controller - 103
unit 4 - 004 no remote controller
unit 5 - 005 (master) - remote controller - 105
unit 6- 006 (slave) - no remote controller
unit 7 - 007 remote controller - 107
Can anyone shed any light on the BC box control?
Should the LED be on upon powering up or does the LED only come on upon system transmitting correctly?
This is a very strange phenomenon and don't know if the system will require a software re-boot.
Look forward to any advice.
Regards
Jase
2) BC Controller : CMB -P108V-GA
3) 7 x fan coils
4) AG 150 Centralised controller
Been having problems with commissioning the above system.
Experiencing voltage drops on the M-Net transmission.
Reading 29.4 Vdc @ the M-Net board on outdoor unit but upon testing voltage inside at fan coils the reading drops to around 25 Vdc.
It's not a long cable run. Have even replaced the cable but not much joy. Prior to changing out the cable there was 2 fan coils with no LED's showing on the PCB's. Also no LED at the BC box. Checked power supplies and found all to be satisfactory. Power being supplied from transformers to PCB's too!
Once the cable was replaced the LED's for the fan coils came on but still no LED on the BC box.
The AG 150 is not showing much too. It shows the address settings of the fan coils and local remote controllers and is in alarm condition. Fault is '6607'.
The control for this system is being used on the M-Net set up. The remote controllers are wired in on the M-Net transmission.
There are only 4 x remote controllers being used and all system is addressed.
Address:
unit 1 - 001 no remote controller
unit 2 - 002 remote controller - 102
unit 3 - 003 remote controller - 103
unit 4 - 004 no remote controller
unit 5 - 005 (master) - remote controller - 105
unit 6- 006 (slave) - no remote controller
unit 7 - 007 remote controller - 107
Can anyone shed any light on the BC box control?
Should the LED be on upon powering up or does the LED only come on upon system transmitting correctly?
This is a very strange phenomenon and don't know if the system will require a software re-boot.
Look forward to any advice.
Regards
Jase