PDA

View Full Version : Haier error



for
05-01-2011, 03:07 PM
Hi! I have a problem with Haier inverter, one time it showed error 14. I turned it off, then started again, and everything was normal. What does it mean?

Thanks.

chillin out
05-01-2011, 07:34 PM
This is all I have on these...

Haier Fault Codes
1 Flash = Indoor Temperature Sensor faulty
2 Flash = Indoor Coil Temperature
3 Flash = Outdoor Temperature Sensor Faulty
4 Flash = Outdoor Coil Temperature
5 Flash = Over Current Protect
6 Flash = Pressure Protect (HP/LP)
7 Flash = 3Phase Protection
8 Flash = Communication Trouble between Wired Remote and indoor unit
9 Flash = Communication Trouble between indoor / Outdoor unit
10 Flash = High Condensate Level

Chillin:):)

Sserrviceman
06-01-2011, 04:50 AM
If it is simple 14 ( for example model HCFU-42CF03 with wired controller YR-E2) - "High pressure abnormal" - High pressure switch acts 3 times in 30 min.
If it is - E14 ( for example model HSU-09/12HVA103) - "Indoor fan motor malfunction" - breaking of wire inside the fan motor, breaking of the fan motor lead wires, faulty indoor unit PCB or Hall IC.

for
06-01-2011, 06:16 PM
Thanks a lot, actually it's hsu... simple e 14. It shoul'd be the fan, thanks.