View Full Version : 5 ton kws



ostaine
03-01-2011, 07:54 PM
Did a power consumption reading on a 5 ton, single phase, A/C unit and the total power consumption for the Evap and condenser was 4.36kw. Is this reading normal?

Brian_UK
03-01-2011, 07:58 PM
Sorry, don't know.

What does the data plate on the unit say?

ostaine
03-01-2011, 08:06 PM
there is no refrence to the power consumption , but its a five ton single , 208 volts unit, compressor running and evap fan on high

DTLarca
03-01-2011, 08:09 PM
Did a power consumption reading on a 5 ton, single phase, A/C unit and the total power consumption for the Evap and condenser was 4.36kw. Is this reading normal?

Sounds about right - the unit is probably not running at design full load. The numbers are about where we would expect them to be with the unit running say 70 to 80% Loaded - meaning the return air and outdoor air enthalpy's are low enough to, in a combined fashion, amount to less that full design load conditions.

ostaine
05-01-2011, 01:24 AM
Waiting for a warm day to do recording of with reps from utility company using Fluke test gear. will also record ambient and room temp

ostaine
06-01-2011, 01:01 AM
single 5ton a/c , compressor running, condenser fan running, evap fan on high,
Ambient 88.5 F
Power consumption 4.352 Kw
Room Temp 71.6 F

ostaine
08-01-2011, 07:02 PM
Here's what on the nameplates.
Condensing Unit
Make : Goodman
Model : CKL60 - 1L
A/C Volts : 208/230 phase 1 Hertzs 60
Factory Charge oz R22 115
COMPRESSOR
Make : Copeland ZR57KC-PFV-250
RLA 25 A LRA 150
Evaporator
Model #UG060CKA2LACL2
SERIAL # 50050072-4118

ostaine
08-01-2011, 07:04 PM
Here's what on the nameplates.
Condensing Unit
Make : Goodman
Model : CKL60 - 1L
A/C Volts : 208/230 phase 1 Hertzs 60
Factory Charge oz R22 115
COMPRESSOR
Make : Copeland ZR57KC-PFV-250
RLA 25 A LRA 150
Evaporator
Model #UG060CKA2LACL2
SERIAL # 50050072-4118