Hello experts,
I need make island case with built-in condensig unit and capillary tube.
The air temperature inside may vary from minus 6 C to plus 6 C.
Should I use LBP or MBP Embraco compressor for condensig unit ?
Which must be evaporation temperature?

Thanks for any advice

botrous
09-08-2005, 11:01 PM
Tralex , i didn't understand what you want to build . . . please explain

tralex
10-08-2005, 11:09 AM
Hello botrous,
I'm sorry for my inefficiency to explain what I want.
Now I drew my question.
Thank you

Abe
10-08-2005, 01:09 PM
You need MBP or LBP assuming you want to evaporate around -16C
to achieve -6C

You need to check Embraco table for that compressor to see if it can achieve the required duty at that evap temp

botrous
10-08-2005, 06:49 PM
I agree with Ayub . . . send an email to the Embarco and they can help you select the right compressor for your application or see the Embarco tables

Kevin S
14-08-2005, 12:08 PM
You also need to check the condenser size if you intend using the existing one. The safest would be to use a standard condensing unit sized to the (new) capacity of the existing evap. Remember the evap will give slighlty more capacity at the high temperature (depending on the delta T of course).