View Full Version : panasonic inverter cu/cs12 ckp



dance
27-12-2010, 11:06 AM
please help when i start air con.on cooling mode he works very good but when is on heating mode he works about 3 minutes and turn off after 3min. he start again. 3min.start 3min off the pressure is good when pressure is 20bars current is 4 A ON heating mode compressor stop where is problem air.con. don't displayed any errors.:off topic:

sedgy
27-12-2010, 06:34 PM
hi dance. tell me is the set point < on heating < 2c more than the room temp,? sedgy,

dance
27-12-2010, 07:49 PM
I found problem. sensor of the heat exchanger on indoor unit.

sedgy
28-12-2010, 09:11 AM
ok dance , well done, thanks for letting us know, sedgy,

paolinka
02-01-2011, 12:19 AM
any picture of sensor - where is itr? thx!