View Full Version : Carrier 30GX please help



Morne
24-12-2010, 01:00 PM
Hi guys i am new to this forum and looking forward to a lot of Q and A.
I am working on a Carrier 30GX, on the display it shows "override". Only one compressor is running. I had a look in the manual and it says Limit: The operation conditions do not allow total unit operation. Can anyone please tel me what i should be looking for?

Grizzly
24-12-2010, 02:04 PM
Hi Morne and welcome to the forum.
Please refer to the attached pdf.
Read section 5.8
Which is an explanation of your issues.
Grizzly

Morne
24-12-2010, 04:03 PM
Hi thank you for your reply. I had a look at that section, i looked on the chiller setpoint menu 2 (no5) and it is set to 100%. I also looked at inputs menu 2 (no4) and found this contact to be open. On the connection terminal no73 and no74 is not connected.

Grizzly
24-12-2010, 05:17 PM
Hi Morne.
Is this errant chiller stand alone or is it normally ran via CCN.
Also what version of Prodialog do you have?
Grizzly

Morne
24-12-2010, 07:52 PM
Hi it is a stand alone, it only gets a start signal from the bms. I am not sure what vesion prodialog i got.It ran fine for almost 7years now.

Grizzly
24-12-2010, 09:15 PM
If it's that old and stand alone, what I was thinking is redundant.
Maybe some of the older (and Carrier based) guys on the forum may be able to help?
Grizzly