View Full Version : Design of compressor
ritesh19481
23-12-2010, 11:29 AM
dear all,
ii just want to know the capacity of compressor and its motor size for manufacturing a 32 tos ice from water inlet temp 30'c and ice temp -5 'c at condensing temp is 40'c and evaporation temp of brine tank is -12 'c ...pleasae help or suggese
NoNickName
23-12-2010, 12:24 PM
32000 Kg x 35K = 1.120.000 Kcal
Assuming you want to produce 35 tons of ice per day, the average cooling capacity required is 46666 Kcal/h = 54kW.
A suitable compressor with R404A refrigerant would be Z 25 103 Y from Frascold or 6H_25.2Y-40P from Bitzer or equivalent 25HP, 105m3/h compressor from other manufacturers
D.D.KORANNE
23-12-2010, 01:03 PM
if you are talkin about block ice which i guess , you would roughly need about 35 tons by 1.6 TR compressor .
Alternatively , precool the water from 30 deg c to say 10 , will improve the quality of ice .
NoNickName
23-12-2010, 01:16 PM
you would roughly need about 35 tons by 1.6 TR compressor .
Would you please elaborate on this? How a 5kW cooling capacity compressor is going to freeze 32 or 35 tons of water in a any reasonable time?
chemi-cool
23-12-2010, 02:55 PM
Would you please elaborate on this? How a 5kW cooling capacity compressor is going to freeze 32 or 35 tons of water in a any reasonable time?
Very slow....:D
Brian_UK
23-12-2010, 07:51 PM
Sounds like the UAE is about to get an ice-rink.
ritesh19481
25-12-2010, 07:59 AM
Tjank x to all can i use kirlosker compressor Kc 4 model ,flow rate is 580 m3/hr ,
NoNickName
25-12-2010, 09:55 AM
Yes, you will freeze the 32 tons of water in 5-6 hours with that compressor @ 1000rpm. But you can't use R404a because the compressor max pressure is 21 bar, so you have to use R134a.
yacoub
26-12-2010, 04:19 PM
;)thank you
Lloyd Nhenga
22-01-2011, 08:20 PM
how to calcuate refrigeration compressor capacity using its details