Hello everyone, I have a problem with a Climaveneta water chiller used for air con on a boat.
It has two copeland D4DJ4 300X compressors and the electronic key pad is climaveneta CVM20.
It used to work with comp 2 as master and comp 1 as slave. In hot conditions it ran comp 2 until the chilled water rose above a certain diff over the set point then comp 1 would kick in and and help lower the chilled water until it nearly reached the set point then comp 1 would cut out leaving comp 2 running alone.
Either comp 2 would bring the water temp down to set point or the water temp would rise and comp1 would kick in again.
The chief engineer just called me and says that the system now only runs one compressor at a time even if they are both being asked to run and switches between comp1 and comp 2.
I told him to check the parameters in the menu and make sure that "PRESENCE OF SLAVE" was flagged.
I am awaiting his response and thought I would come here and see if anyone has had a similar problem.
Thanks
Expat
It has two copeland D4DJ4 300X compressors and the electronic key pad is climaveneta CVM20.
It used to work with comp 2 as master and comp 1 as slave. In hot conditions it ran comp 2 until the chilled water rose above a certain diff over the set point then comp 1 would kick in and and help lower the chilled water until it nearly reached the set point then comp 1 would cut out leaving comp 2 running alone.
Either comp 2 would bring the water temp down to set point or the water temp would rise and comp1 would kick in again.
The chief engineer just called me and says that the system now only runs one compressor at a time even if they are both being asked to run and switches between comp1 and comp 2.
I told him to check the parameters in the menu and make sure that "PRESENCE OF SLAVE" was flagged.
I am awaiting his response and thought I would come here and see if anyone has had a similar problem.
Thanks
Expat