View Full Version : Liquid Float Drainers use in Hot Gas Defrost



redbos
14-12-2010, 08:30 PM
Hello everyone,

What is everyone's thoughts on Liquid Float Drainers and their use in Hot Gas Defrost? Do they work well? What issues should one look out for?

Any insight is much appreciated as I'm a newbie in the industrial refrigeration arena.

Regards

Magoo
15-12-2010, 02:52 AM
Hi Redbos.
welcome to the forum.
Firstly, hot gas is more like cool gas by the time it reachs the evaporator, with suction pressure regulation etc., the evap becomes a big condenser, so draining excess liquid is necessary. So long as drain valve is sized correctly no problems, oil draining will happen at same time, the oil can clogg up the float and orifice though, and not drain excess liquid. So when system changes over, it can create a flood back.

redbos
15-12-2010, 05:46 PM
So it sounds like if they are installed correctly, they should work well.

From an energy standpoint, how do Liquid Float Drainers stack up to other methods of defrost?

Sandro Baptista
15-12-2010, 06:12 PM
the WITT have high pressure float regulators, and are the "HR".

Segei
16-12-2010, 03:08 PM
Definitely liquid drainers are better than back pressure regulators, because they drain the liquid and don't pass the gas. Blow by gas will reduce plant efficiency. However, liquid drainers are more expensive than BPRs.

Sandro Baptista
16-12-2010, 03:55 PM
Definitely liquid drainers are better than back pressure regulators, because they drain the liquid and don't pass the gas. Blow by gas will reduce plant efficiency. However, liquid drainers are more expensive than BPRs.

Plenty agree with Segei