PDA

View Full Version : 600TR Carrier chiller vacuumization



avsuku
13-12-2010, 02:31 PM
I am attending a Carrier screw chiller of 600TR capacity. The cooler pipes brocken and water entered into the system. While vacuum iam getting only 2500 microns and company insisting for 500 microns. Last 5 day iam running the vacuum of 350lps capacity and there is no improement. please post your ideas

thank you

casstrig
13-12-2010, 02:52 PM
I had a similar problem but was lucky that there was a steam boiler in the same plant room and was able to pass hot water through whilst vacuuming,in your case I would change the vacuum pump oil every few hours as if it becomes saturated with moisture it will give off moisture limiting the level of vacuum.

serviceman
13-12-2010, 03:08 PM
using a moisture trap and performs sweeps nitrojeno

cool_kid
13-12-2010, 09:08 PM
Have you tried a triple evacuation?

dave hammo
19-12-2010, 07:15 AM
changing the vac pump oil regularly is a must with moisture in the system plus using nitro to triple vac as previusly mentioned

nike123
19-12-2010, 07:43 AM
http://www.refrigeration-engineer.com/forums/showpost.php?p=206077&postcount=65

dave hammo
19-12-2010, 07:57 AM
love that word VACUUMIZATION!!!