Hi all,
I am having a problem with a GSC OP panel based on the Siemens S7-300 and C7-633.
The problem is that once in a while there is a power failure which once in a while results in an error:
Recovered after a power failure (just about).
The error does not show every time, but often enough for the customer wanting to have it fixed.
I have not been able to produce the error.
Does anybody have an idea about what is causing this behavior?

Regards,
Peter

lavurk
13-12-2010, 02:32 PM
If you can provide UPS power to PLC system.Your problem will be solve.

petter78
22-12-2010, 04:51 PM
Are you sure? The PLC will still get noticed about the power failure and might still go into manual mode. Are you sure a UPS will solve the problem?