06-12-2010, 09:25 PM
Hello everybody, i need some help.

I've been looking at a Samsung RVXVRT140GE DVM, conected to a Samsung RVXVRT120GE DVM.

When I arrived on site i was informed by the customer that the fan coils are running but only circulating air.

The condenser is showing an E-214 fault (MCU's not matching outdoor units PCB setting) The MCU dial switch is set to 5, with number of fan coils connected 20.

I hit the K3 switch on the condenser PCB to reset the system then let it go through its process, still E-214 appearing.

As this is a newish contract for us I went through the whole building and identified all the MCU's, I found the following:

3rd floor 4x units /1x MCU Set as No00-showing E214
2nd floor 5x units /1x MCU Set as No01-showing 65C8
1st floor 4x units /1x MCU Set as No02 -showing E214
1st floor 3x units /1x MCU Set as No03 -showing 67C8
Grd floor 4x units /1x MCU Set as No04 -showing E214

With the units showing the above the system will not run, the MCB's just seem to keep going through the setting up stages??

I decide to try to elimnate what i suspect are the faulty units, so i shut down MCU's 01 & 03, then reset the condenser PCB to 3 MCU's. The system goes through it cycle, i am then able to run the remaining 3 MCU's and the system runs ok.

From the above it seems that MCU's 01 & 03 PCB's are possibly faulty? This is the first Samsung ive worked on, seems a little strange that 2 PCB's would fail together.

Have any of you any experience on these Samsung RVXVRT140GE DVM, is there anything else I can try. I dont want to replace PCB's if I dont have to.

Also can anyone let me know what the 67C8 that the MCU is showing means.

Samsung technical seem very hard to get hold off, if you have a recommendation of someone I could talk to that would be most appreciated.

Thanks in advance

superswill
07-12-2010, 12:32 AM
Gary,

67c8 means normal operation, 67c8 may mean command cooling valve xyz open ect just really shows control logic

sounds like two faulty PCB's to me, one thing to check is the port dip switch's A-D are set to on and not off but then swap one of the PCB's from the working to prove a point.

odd why two would go, check power supply before changing

tech support and spares available from:

The Air Conditioning Centre – HRP T. 01753 495715
159 Edinburgh Avenue, Slough Trading Estate,
Slough SL1 4UE F. 01753 495711
E. slough@hrpltd.co.uk

Dysk Air Conditioning T. 01582 463420
Unit 7, Allied Business Centre,
Harpenden, Herts AL5 4UT F. 01582 765986
E. sales@dysk.co.uk

Easy Air Conditioning T. 0870 111 4880
262-264 Baldwins Lane,
Hall Green, Birmingham B28 0XB F. 0121 746 3505
E. iinfo@easyairconditioning.com

Freedom Air Conditioning T: 02380 653283
Unit 5, St Georges Industrial Estate, Goodwood Road, Eastleigh, Hampshire SO50 4NT F: 02380 653285
E: sales@freedomac.co.uk

Gallant Air Conditioning T. 01623 646640
Gothic House, Barker Gate,
Lace Market, Nottingham NG1 1JU F. 01623 623931
E. enquiries@gallantairconditioning.com

Logicool Air Conditioning Distribution T: 01283 218277
Unit 4, George Holmes Business Centre, George Holmes Way, Swadlincote, Derbyshire DE11 9DF F: 01283 229352
E: sales@logicool-ac.com

RDL T. 01 4506001
Unit 6D, Ballymount Industrial Estate,
Walkinstown, Dublin 12 F. 01 4503676
E. sales@dublin.rdl.ie

Ultimate Air T: 01883 745001
Godstone Vineyard, Quarry Road, Godstone, Surrey RH9 8DQ F: 01883 745009
E: sales@ultimateair.co.uk