PDA

View Full Version : Hoshizaki Ice Machine



matt.yelland
04-12-2010, 04:36 PM
KM-1300SAF-E. J10006. R404A.

Hiya all,

I got a call out friday night to a ice machine not creating any cubed ice. When I got there, both evaps were iced up solid. I fully defrosted and checked the hot gas solenoid valve. Working ok, suction pressure at 6.5 bar. Ran on a harvested, suction pressure 3.5 bar. I cleaned the condenser and carried out an acid clean....

Im going back early next week to check on the unit again as site are saying that the unit has been a problem for about 6 months.

Just wondering if anybody can think of anything else that I may need to check...

Many thanks

Matt

dennycrane
05-12-2010, 12:22 AM
No offense, but your post is a bit confusing.

What was your back pressure when the machine was trying to make ice?

matt.yelland
05-12-2010, 06:57 PM
Hiya dennycrane,

Suction pressure when trying to make ice is 3.5 bar.

Suction pressure when on a defrost is 6.5 bar.

None taken, but how is that confusing....