03-12-2010, 10:19 AM
Hi guys wondering if you could point me in the right direction.
I attended a site a few months ago and looked at a multi split system with 2 x indoor units.
In full heating it runs very well but is pulling 16 amps from outdoors ( power to outside then interconnecting to indoor units)
Filters and coil are cleaned and ok. System heats the room up fine. With nothing out of the ordinary. But since and before my visit the client has found in the morning when they arrive and get the infa red controller and turn system on what ever mode the breaker trips straight away. I have since been to site turned system off and turned breaker back on and turned system on and again system runs perfect. In both modes. Since this visit it has tripped again.
Been told its prob compressor but i have had it running in fill heating in -2 ambient temp and below and it was fine. It has ran for 2 years with no problems what so ever.
I have checked refrigerant charge and its all good.
I can't remember model numbers but can get them at weekend. He two indoor units are radiator type ones.
With infa red controllers and I have checked both units for faults with the controller bleep thing and says there is none.
It's literally trips when they turn remote on. I'm thinking it must be a wrong problem. On the power side as the interconnecting seems all good.
Thanks in advance
Regards weidit
I attended a site a few months ago and looked at a multi split system with 2 x indoor units.
In full heating it runs very well but is pulling 16 amps from outdoors ( power to outside then interconnecting to indoor units)
Filters and coil are cleaned and ok. System heats the room up fine. With nothing out of the ordinary. But since and before my visit the client has found in the morning when they arrive and get the infa red controller and turn system on what ever mode the breaker trips straight away. I have since been to site turned system off and turned breaker back on and turned system on and again system runs perfect. In both modes. Since this visit it has tripped again.
Been told its prob compressor but i have had it running in fill heating in -2 ambient temp and below and it was fine. It has ran for 2 years with no problems what so ever.
I have checked refrigerant charge and its all good.
I can't remember model numbers but can get them at weekend. He two indoor units are radiator type ones.
With infa red controllers and I have checked both units for faults with the controller bleep thing and says there is none.
It's literally trips when they turn remote on. I'm thinking it must be a wrong problem. On the power side as the interconnecting seems all good.
Thanks in advance
Regards weidit