View Full Version : Daikin C1 Fault



leegally1983
29-11-2010, 05:58 PM
Hi guys/girls
I have a a daikin ducted unit with a c1 fault its a new installation and i cant find this fault code on the daikin sheets, help wud be much appreciated.
Thanks
Lee

troymedhurst
29-11-2010, 06:25 PM
I just text C1 to daikan and recieved the message 'Please ring daikin technical help desk' 08456419200

Never seen this before. Hope it works out ok!

leegally1983
29-11-2010, 06:26 PM
i know ive tried that :(

leegally1983
29-11-2010, 06:27 PM
thats not a angry response altough it looks it

james10
29-11-2010, 07:22 PM
Just checked the Daikin code chart all the "C" codes relate to sensors might be worth checking all the sensors. although it could be one of the elusive secret codes:D

VRVIII
30-11-2010, 11:43 PM
Hi guys/girls
I have a a daikin ducted unit with a c1 fault its a new installation and i cant find this fault code on the daikin sheets, help wud be much appreciated.
Thanks
Lee

C1 fault code indicates a communication error between the indoor unit main PCB (A1P) and indoor inverter fan PCB (A2P). This is indicated and explained within the unit installation manual.

shimceltic
02-12-2010, 07:21 PM
I had this fault on a split. You need seperate power to th indoor as well as the 4 core interconecting to run the fan Daikin said it is ok to piggy back the L N E out of the interconecting

VRVIII
03-12-2010, 08:19 PM
I had this fault on a split. You need seperate power to th indoor as well as the 4 core interconecting to run the fan Daikin said it is ok to piggy back the L N E out of the interconecting

This only applies to sky air units as all VRV indoor units require a power supply.

wozza
03-12-2010, 10:33 PM
You have to check the install manual as to whether you can piggy back off the interconnecting on the skyair units.
Some need a seperate power supply and some dont.

Mabe
09-12-2010, 04:22 PM
The new duct units have an inverterfanmotor and it also need 220Volt power suply for the inverterprint, the contact are there, just wire from L-N (power suply indoor) to L-N inverterprint and C1 wil be gone.