View Full Version : Problems with daikin container



interfrigo_cuki
26-11-2010, 04:56 PM
hi all!!!!!

I have a problem with daikin container LXE10E-A21D,
when i wast went to check it it was showing low presure alarm, i`ve changed the filter dryer and charge it with r-134a and it has start to run, when i went day after to check it it was again low presure alarm i have check for a leak and there was no leak, now the compresor is starting to work only for 2-4 minuts and stoping and there is no alram on display....???????? any sugestions what can it be wrong with it.....
p.s. there is gas in it.

berst regards from pristina, Kosovo

sedgy
26-11-2010, 05:55 PM
short of gas.

roger head
26-11-2010, 07:03 PM
check the quench valve

interfrigo_cuki
28-11-2010, 02:24 PM
sedgy, I have add gas enough but still the same and the quench valve seems to be ok...any idea where can i find manual?

transcold
02-12-2010, 06:49 AM
Check the electronic expansion valve. If this valve open at 10%~12% all the time, you should manully adjust this valve to larger opening. If the opening is not 10%~12%, maybe the bady of EEV is blocked.
additional, check LPT.

Mungo
14-12-2010, 12:57 AM
Hi
Without knowing what sort of pressurers you have a bit differcult but if you have a new TX Valve coil P/N 138143J, I suggest you try. Moisture can get between coil and plunger and freeze stopping plunger from working and shutting valve down. You do not have to recover gas to change coil. Could also be faulty TX valve body P/N 125649J. You will need to pump system down to change this.
Good luck.
Mungo:D

bruisermac
14-12-2010, 01:30 AM
remove the EEV coil and blow out the ice and dirt from the top of the valve. then reassemble it. Make sure your LPT reading and gauge readings are the same. I have seen alet of faulty LPT.