25-07-2005, 08:59 PM
I thought this was interesting:
Got a really old 15 ton carrier split thats been jack legged to the max.
COmpressor contactor has a 240 volt coil.
Someone wired in a 4mfd 440volt capacitor to the coil.
Its paralleled across the coil.
Also... the 240 being applied to the coil also
powers the 3 condenser fans (240 volt, single phase)
Anyone ever see a capacitor wired across a contactor before?
If so... any idea what it supposed to do?
I'm guessing its to keep the contactor from bouncing/jumping since they got the control voltage all
jumbled up with load voltage to the condenser fans. :confused: :D
Brian_UK
25-07-2005, 10:37 PM
It acts as a coil suppressor to stop spikes on the control circuit when the contactor pulls in.
wambat
26-07-2005, 02:56 AM
It acts as a coil suppressor to stop spikes on the control circuit when the contactor pulls in.Too simple, could you be more specific. seems to me to be very unconvential as I have never seen this done before. Why would a contactor that pulls in create a spike. Seems to me that it would deminish the total impedence of the coil and pull in better because of more amp draw :confused:
botrous
26-07-2005, 07:29 PM
Well Wambat , I think that the contactor pulls can create spikes because maybe what we call in french "bobine de fragaire" is deffective , so the contactor start to release and compresses in a very high rate , when his coil is energized , i donno if that's the reason to put a capacitor , but it's sure a certain reason for spikes
Superheatman
26-07-2005, 07:48 PM
Hi...York fit suppressors(small capacitors) across their part wind starter sets very frequently....as Brian said it is expedient when there are pcb's in the circuit as it reduces spikes....dont know why they would fit them on a very old unit though unless someone had seen them elsewhere and decided that they were missing....stranger things have happened!
botrous
26-07-2005, 09:52 PM
I think i found what we are searching for , take a look at this :
http://www.franklin-electric.com/aid/vol16no2.htm
wambat
27-07-2005, 05:34 AM
Botrous, Thanks for the interest and the web site :)
botrous
27-07-2005, 10:28 AM
Welcome Wambat , hope it's useful for you :)
York fitted them because they had a problem with the contactor faces shrinking and causing "no Run" faults on start up (vendor fault) make sure that the contactor that you have is not already internally suppressed as it will burn the coil out. But as Frank said it is to stop spikes when you have electronic controls.
nubbin
21-03-2008, 05:17 AM
Just a note: the web site link is for series LC circuits where the lead/lag current of caps and coils creates higher voltages. A cap across a coil is a parrallel LC circuit. What happens (is also found in digital control cicuits) when the power to the coil is turned off, the magnetic field colapses inducing a voltage back to the control circuit (changes in magnetic fields generate electric current like a generator). The capacitor absorbs the current spike before it attacks the control components. It also reduces Radio Frequency noise and control switch pitting by reducing/preventing arcing at the switch contacts.
NoNickName
21-03-2008, 08:04 AM
It's an old trick. Car manufacturers were installing a capacitor in parallel with the platinum contacts of the spark ignitors (in the 40s and 50s) to avoid dangerous arcing.
Peter_1
22-03-2008, 04:30 PM
Agree with the sparking story but it it is here fitted over the coil and no contacts are closed on the coil, so you don't have sparks over the coil.
paul_h
22-03-2008, 06:08 PM
Agree with the sparking story but it it is here fitted over the coil and no contacts are closed on the coil, so you don't have sparks over the coil.
It's mainly used because of the way PCBs send the signal to the contactor, probably heavily filtered mains cutting off the sine wave due to excessive mains filtering (just guessing as all of them have both the filtered mains and a capacitor). Most domestic units have a cap over the coil. In fact the panasonics had to have a capacitor retrofited over the relay, if not, terrible loud loud buzzing was complained about.
I'm guessing that the buzzing was caused by the relay cycling a million+ times a second (edit: exaggeration BTW), and that wouldn't be good for the contacts and device. But mainly it's not necessary, just covering their bases in case that happens.
Kh1971
23-03-2008, 12:45 PM
thanks botrous please keep shining , you are my star
Regards
Khalid