View Full Version : Capillary Sizing



majortom
23-11-2010, 09:58 PM
Could anyone please help regarding selecting a capillary tube for a single door commercial freezer using a Supco Bullet Restricto Capillary Kit?

The compressor is a Cubigel GP14FB 3/8 HP on R134A but Supco's selection chart does not include this size compressor. The condenser is fan cooled but the evaporator is without a fan.

I have attached Supco's sizing chart.

Any other suggestions to what the capillary size should be or how to size the capillary would be greatly appreciated! :)

Brian_UK
23-11-2010, 10:54 PM
Download Dancap from Danfoss and you can calculate just what you need.

Remember that most cap tube sizing is an experiment.

http://www.danfoss.com/BusinessAreas/RefrigerationAndAirConditioning/Product+Selection+Tools+Details/DanCap.htm

Also, download the specification of that compressor if you don't already have it.
http://www.hawco.co.uk/GP14FB-ECC-Cubigel-R134a-LBP-HST-Compressor_2246_p.aspx

vijitha1234
24-11-2010, 11:17 AM
let me know the test procedure to balance condenser water system for water cooled packages in a multy storied building please

Peter_1
24-11-2010, 10:47 PM
let me know the test procedure to balance condenser water system for water cooled packages in a multy storied building please

What hast his to do wit capillary sizing?
You must post this in the proper section :off topic:

majortom
01-12-2010, 08:55 PM
Thanks for the advice Peter but I am not sure on finding some of the calculations needed with DanCap such as heat load of the system. I presume that the evaporating temp and the return gas temp will give the evaporator superheat differential??

tonyelian
02-12-2010, 06:16 PM
hi
referring to tecumseh its 2 meter 0.036 internal diameter

PRESS
02-12-2010, 06:40 PM
I have always trusted to use the DANCAP program which Brian has prescribed above.

kiwifridgie
22-06-2011, 11:36 AM
1.9m 0.042 for single feed evap on this comp

solenoid
22-06-2011, 07:00 PM
DanCap seems to be a good software, but could someone please let me know, how to estimate the heatload in a easy way for any specifik unit ? For example, it can be tricky to estimate the heat load for a bottle fridge when one wants to change the cap.tube. Kind regards / Tobias

jcook1982
30-06-2011, 01:29 AM
Software or no software. The cap tube primary purpose is to meter the amount of refrigerant getting to a specific part of the refrigerant circuit. So what you need to know is how much flow through the original cap tube and match up a size and length that will do the same.