langy
22-11-2010, 08:29 PM
I was helping commission 3x 12hp outdoor to tripple indoor unit systems today. The other engineer had used the refrigerant circuit rotary switch to address:o,instead of address rotary switch on the indoors .
Obviously systems would not fire up. We quickly rectified two systems (fault code 03), but I noticed smoke coming from third system outdoor inverter board.
I quickly switched power off, checked all wiring and examined inverter board.
All the external wiring is correct, all around the small relays on the board blackened.
I have switched off until tomorrow so I could finish commissioning the other two systems.
Has anyone had this problem or got any ideas???
Added day later.
Got it wrong its the noise filter board!!
Hitachi technical say it must be a power supply problem...checked over with electrician...no problems found.
New board ordered.