paul_h
16-11-2010, 01:27 PM
I've got an older pana ducted, it's a but of a cross between the really old units and the newer ones.
The indoor is a CS-71E91ER and is built like the really old ones, the outdoor is a CU-71C52HP and is built like the bbp8 series of about 6-8 years ago ( the wall controller is the same to the slightly more recent bbp8 series too) So outdoor PCB and wall controller similar to what I'm used to.
Anyway, this thing just cuts out after running fine for a few minutes. There's no operation LED flash on the controller or code*, or fault logged on the outdoor LEDs.
It cuts out set to 16C with 30C ambient, and cuts out on test mode too
*In the memory of the test fuction on the indoor controller, it brings up F33, but like I said, that's memory and I don't know how to clear it and the compressor amps is fine and no faults on the outdoor PCB anyway or the indoor controller flashing out on fault.
How do you clear the indoor controller error history? I really wish I could clear it so be sure of what is and old fault and what is new (the compressor was changed months ago apparently)
From memory may be a bad indoor thermistor (coil or air) that causes them to cut out without any error codes, but hoping someones got info on this slightly older than I'm used to pana.
Is stef out there still?
The indoor is a CS-71E91ER and is built like the really old ones, the outdoor is a CU-71C52HP and is built like the bbp8 series of about 6-8 years ago ( the wall controller is the same to the slightly more recent bbp8 series too) So outdoor PCB and wall controller similar to what I'm used to.
Anyway, this thing just cuts out after running fine for a few minutes. There's no operation LED flash on the controller or code*, or fault logged on the outdoor LEDs.
It cuts out set to 16C with 30C ambient, and cuts out on test mode too
*In the memory of the test fuction on the indoor controller, it brings up F33, but like I said, that's memory and I don't know how to clear it and the compressor amps is fine and no faults on the outdoor PCB anyway or the indoor controller flashing out on fault.
How do you clear the indoor controller error history? I really wish I could clear it so be sure of what is and old fault and what is new (the compressor was changed months ago apparently)
From memory may be a bad indoor thermistor (coil or air) that causes them to cut out without any error codes, but hoping someones got info on this slightly older than I'm used to pana.
Is stef out there still?