View Full Version : problem when defrost, always high pressure



emass814
12-11-2010, 03:23 AM
dear all, please help me. i just finished making a new tube ice maker, but there is a problem, everytime the machine defrost and the ice came out, the machine get high pressure. i must restart again, but when it restart for about 5-9 minutes, it defrost again. the normal time for defrost are around 20-25 minutes. Please help me and give an explanation why this can happen. If possible please give the diagram picture and the scheme of the machine system.Thank's for helping me.

Sandro Baptista
12-11-2010, 03:37 AM
The defrost system is with one tube and return by the wet suction or is a two tubes system, which the hot gas return goes to the condenser?

emass814
15-11-2010, 02:20 PM
@sandro : thank's for the reply. The defrost system uses 2 tubes and the hot gas goes to another pipe. Can you please send me the picture / scheme of the system ?

Sandro Baptista
15-11-2010, 02:42 PM
Sorry...Isn't 2 tubes at all » one goes with hot gas and the other with the returned mixed vapor and liquid?

Brian_UK
15-11-2010, 10:22 PM
It is your design so please provide present scheme layout so that we can comment on it.

emass814
22-11-2010, 12:59 AM
@Brian : thank you, about the layout scheme, can you please tell me how to post it ? since I am a newbie here.

Magoo
22-11-2010, 01:06 AM
Hopefully the compressor is unloading during hot gas defrost harvest time.

RANGER1
22-11-2010, 07:08 AM
Sounds like a Frick ice machine .
Does it make ice inside or outside of tubes?
Hopefully a schematic will be posted soon .

emass814
25-11-2010, 01:40 AM
@ Ranger1 : thank's for the reply. It makes the ice inside the tubes.

Magoo
25-11-2010, 02:28 AM
Harvest cycle should be around 5 minutes, and tube ice should start dropping with vessel press/temp at or around +5.0'C.