PDA

View Full Version : Alarm 56 in Chiller Carrier 30RA



tambymah
11-11-2010, 10:15 AM
Hi all,

I have faced the Alarm 56 in Chiller Carrier 30RA, but whe I look up in the catalog I find nothing about this Alarm.

Please advise.

Thanks in advance.

Tamby
Syria
00963955978515

acnerd
11-11-2010, 01:07 PM
If you go into the alarm history menu on the chiller itself, it should tell you what the alarm is?

james10
11-11-2010, 05:53 PM
when displaying the fault press enter and the alarm description will be displayed

hoodemar
12-11-2010, 07:36 AM
It can be the reason for ur unit.
"Excessive temperature in the
control box "
if not pls write the full model number

Gibbo
13-11-2010, 08:28 AM
There are 2 versions of this chiller version A has alarm 56 and version B does not. You probably have the wrong manual.

Willem V
13-11-2010, 11:47 AM
you're sure it's a 30RA and not a 30RB for example, do you've the exact type and year of make?

Willem V
13-11-2010, 06:26 PM
Gibbo was wright, it's in 30RA version A, and means:

Excessive temperature in the
control box (only for “Option 16”
units)

Willem V
13-11-2010, 06:30 PM
and option 16 is high ambiant version

Willem V
13-11-2010, 06:32 PM
search for Carrier information and the manuals on:
http://eto.carrier.com/lit.asp