View Full Version : Design condensing temperature for Dammam, Saudi Arabia
Sigaar
10-11-2010, 02:18 PM
Good day,
What would be the optimal, design, condensing temperature for an R717 plant in Dammam, Saudi Arabia?
Regards,
NoNickName
10-11-2010, 02:52 PM
60°C for air cooled condenser
Segei
11-11-2010, 11:42 PM
Good day,
What would be the optimal, design, condensing temperature for an R717 plant in Dammam, Saudi Arabia?
Regards,
What is the design wet bulb temperature in this area?
charlie n
12-11-2010, 12:15 PM
I worked in Dammam for years. All of the plants I worked on were ammonia systems with evap. condensers. We had no problem designing for 40 degrees condensing & no problem maintaining 35 to 38 degrees saturated condensing temperature in practice. Summer temperatures can reach 50 for almost a month so air cooled condensing should be designed for at least 60.
Sigaar
16-11-2010, 08:37 AM
Thank you Charlie