why after i repalce the outdoor unit fan motor,the error code e3 come out and the unit faulthy agian?....
E3 is high pressure alarm. I asume u changed the fan because it was faulty and causing the alarm. U sure it's not just a faulty pressure switch? Dies the unit start and run? Does your new fan run?
km0110
05-11-2010, 11:01 AM
new fan run in slow speed.than stop soonly..at last the high pressure come out
What is the head pressure? Is the coli clean? Good airflow?
km0110
05-11-2010, 11:05 AM
ya the coli is clean
What is the head pressure when the unit cuts out?
El Padre
06-11-2010, 05:42 PM
Have you checked the discharge transducer? If you ask Daikin for a manual you can check the transducer input on a graph. If not measure the voltage between the black and white cables and post what you find, obviously check with gauges what actual pressure is.