in the work place theres a produce case hussman multiple decks (2) 8 fts lengh 2 fans 1 for evaporator coil,the equipment is charged with the right charged but i cant get a low temp just 44 degrees (f) not less, so i dont know, if its that termostatic expansion valve is bad or some other problem, i hope your help thanks.

mikeref
05-11-2010, 07:02 AM
in the work place theres a produce case hussman multiple decks (2) 8 fts lengh 2 fans 1 for evaporator coil,the equipment is charged with the right charged but i cant get a low temp just 44 degrees (f) not less, so i dont know, if its that termostatic expansion valve is bad or some other problem, i hope your help thanks.
Theicehunter, can you be sure the evaporator coil is completely free of ice? Gas type/pressure etc required.. mike.:)

NoNickName
05-11-2010, 07:44 AM
The setpoint is?

That's too cold
09-11-2010, 10:01 PM
I presume the sight glass is full. After checking the evap coils for no ice,
Check the super heat at each coil,
Check thermostat setting,
Check LP cut-out setting.