View Full Version : Sporlan Expansion Valve



Ashwin123
03-11-2010, 09:08 PM
Hello everyone,

This is my first post, so I hope I won't be getting too much out of the subject.

I am having trouble identifying two Sporlan expansion valves which I will be replacing with Danfoss. I have to replace with Danfoss as I have a time limit for delivering the work.

I managed to get the tonnage for both valves except for the thermostatic charges. Would anybody be able to help me with identifying the thermostatic charges C, L and Z?

It has already been 2 days and since I posted my request to Parker and still no reply.

Thank you.

CanadianIce
03-11-2010, 10:09 PM
What temps are the evaporators operating at?

C Ice

Brian_UK
03-11-2010, 10:21 PM
Sporlan TEV documents here, see doc 10-10 and 10-9.

EG, C charge for 50°F to -10°F
Z charge for 0°F to -40°F

http://www.sporlanonline.com/tevs.shtml

Danfoss charge data
http://www.danfoss.com/North_America/BusinessAreas/Refrigeration+and+Air+Conditioning/Literature/RA_Documentation.htm?CatalogKey=RA-6110f877-1a86-416c-a538-685d2ebcbfd7-en-US:RA-6aa56192-f7e6-4793-b7f9-4c2fa908cc23-en-US&DocumentType=All&Language=en-US

Click on type T2 / TE2 614KB.

That's too cold
16-11-2010, 10:21 PM
Here is another site http://www.sporlanonline.com/

charlie n
17-11-2010, 12:38 PM
The L charge is temperature dependent and not so responsive to pressure change. It is intended for use in larger ammonia systems with multiple evaporators where a change in the flow through one expansion valve has almost no effect on suction pressure.

Ashwin123
07-01-2011, 09:08 AM
Thanks a lot, it was for an ammonia application, but single circuit. It contained about 43 individual circuits. We had them ordered from Parker and it took about 3 months to arrive.

JSakata
31-01-2011, 06:55 PM
Ashwin123,

Do you mind giving us the details on the Parker Tx valves for ammonia?

Happens to be that I'm looking for Tx valves to repalce old Sporlan Tx valves

Thanks, Josue