Dear sir,

I have a customer the use chiller 30HXC, but near by have alarm compressor star delta. could you help me to fix it. I know that maybe the start timer have some problem or timer delay on board not right, and I also check the motor insulation, voltage supply every thing ok.

Thanks & Best Regards.

Nguyen Do Anh Tuan.

goshen
30-10-2010, 06:13 PM
Dear sir,

I have a customer the use chiller 30HXC, but near by have alarm compressor star delta. could you help me to fix it. I know that maybe the start timer have some problem or timer delay on board not right, and I also check the motor insulation, voltage supply every thing ok.

Thanks & Best Regards.

Nguyen Do Anh Tuan.
Hi are you sure it is star delta ?
i have seen all kinds of starting methodes on these units.
if it is a star delta you can dissconnect motor cables as said in one of the above threads and dry run it to see where the problem is.motor or starter,good luck
:D

martua jambak
31-10-2010, 07:44 AM
Hi Tuan Nguyen,

Chiller 30HXC uses soft starter for starter, it's easier to know your problem if you can tell me what is the alarm number?

Regards,
Martua