View Full Version : Stal vertical screw compressor
Kota.Kumar
25-10-2010, 09:29 PM
Hi,
We have vertical screw compressor of model STAL MINI MK2 , we did not use the compressor for last 18 years, we want to run the compressor with R22.
When we started today it was taking 430 amps instead of 230 amps.Is it safe to run the compressor, with out damaging the motor and screws.
Also suggest us who can provide us the spare patrs for above model compressor.
how many hours of work it has? did you open the compressor, 18 years it is a lot of time !
Grizzly
29-10-2010, 06:48 AM
You are certainly going to do damage.
No question!
Switch off and seek Help.
I hope you have a good fire Alarm system?
Grizzly
Kota.Kumar
29-10-2010, 02:48 PM
Not a single time run.
After running for 1 minute it is takimg normal amps.
Can you tell me spare parts suppliers for this compressor
Grizzly
29-10-2010, 02:58 PM
Not a single time run.
After running for 1 minute it is takimg normal amps.
So you could not say this on your original post?
Look up Sabroe Dealers for spares
Grizzly
Kota.Kumar
29-10-2010, 04:32 PM
Coul dyou please tell me what preventive maintenance programme I have to follow for this STAL vertical screw compressor.
What type of break down problems I can anticipate on regular running of this compressor.
Grizzly
29-10-2010, 04:46 PM
Apart from oil filter changes approx, every Year dependant upon hours run.
They are very very reliable.
Provided it is not being ran outside it's design parameters.
But you need a maintenance person to look after it.
(Monitor Oil Diff Pressure.)
I don't think Company Director qualifies, unless your business is refrigeration of course.
Grizzly
Kota.Kumar
29-10-2010, 05:43 PM
We want to make IQF fruits and vegetables.
Plant capacity is 1500 kgs per hour.
How do I calculate its refrigeration laod.
Say for Pineapple.
Tks
750 Valve
06-11-2010, 08:17 AM
We want to make IQF fruits and vegetables.
Plant capacity is 1500 kgs per hour.
How do I calculate its refrigeration laod.
Say for Pineapple.
Tks
Pay someone to do it.
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.