Vapor compressor chilled brine plant:
30 TR capacity, -25 C is the required output
Problem: Temperature is not going beyond -14 C
Brine: 50% - MEOH + 50% - Water
SPG: 0.93
Refrigerant: Ammonia
Chiller Type: Shell & Tube, 6 pass
Compressor Discharge Pressure: 12 kg/cm2
Compressor Suction Pressure: 0.15 kg/cm2
Difference in Temperature around chiller: 1.5 C
Chiller Area is 45 m2