View Full Version : Required temperature output from chiller is not obtained



Bharat812
25-10-2010, 09:34 AM
Vapor compressor chilled brine plant:
30 TR capacity, -25 C is the required output
Problem: Temperature is not going beyond -14 C

Brine: 50% - MEOH + 50% - Water
SPG: 0.93
Refrigerant: Ammonia
Chiller Type: Shell & Tube, 6 pass
Compressor Discharge Pressure: 12 kg/cm2
Compressor Suction Pressure: 0.15 kg/cm2
Difference in Temperature around chiller: 1.5 C
Chiller Area is 45 m2

NoNickName
25-10-2010, 01:44 PM
heat load excessive or cooling capacity insufficient.

Bharat812
25-10-2010, 01:56 PM
No excessive heat load because it is under recirculation mode from tank to chiller to tank. Cooling capacity is sufficient because liquid ammonia from condenser is at 38 C

Emmett
25-10-2010, 02:39 PM
Cooling capacity is sufficient because liquid ammonia from condenser is at 38 C[/quote]:rolleyes:
Huh? I am not an ammonia guy but this dosnt seem to make sense, someone please explain

NoNickName
25-10-2010, 06:17 PM
Both concept don't make sense at all.


No excessive heat load because it is under recirculation mode from tank to chiller to tank

So, what is the heat load then


Cooling capacity is sufficient because liquid ammonia from condenser is at 38 C

I can't see any relation between liquid temperature and cooling capacity