24-10-2010, 09:05 AM
Hi all,
Can I ask a probable silly question?
I have just bought 2 10year old lorry units for our farm and need to know how to use the timer function on the cab command, is says set for 7m on and 45off but the engine still runs all the time, we use these as we don't have electric to the farm but thought that their engine would start and stop as and when it needed to and not run all the time.
also when set to temp start, should it again start up and stop when required?
Thanks in advance
Marc
clivemtk
24-10-2010, 10:44 AM
is this unit set for start stop on the incab control
abbsnowman
24-10-2010, 04:31 PM
If controll is set for auto start stop and unit continuosly runs, check the water temp sensor and battery voltage. They as well as box temp must be satisfied before unit will shut off.
swansea-turkeys
24-10-2010, 06:37 PM
i've pressed the button that looks like a face without a smile which say auto start stop but it doesn't seem to do anything, is there another way?
Thanks
Marc
swansea-turkeys
24-10-2010, 06:39 PM
and both water and fridge temps are good, battery volts at 14.1? should it be a bit more?
thanks
marc
Check on Function change the function Auto Op or Manu OP. It Must be set on " AUTO OP" otherwise the unit starts on S/S but don't stop.
You have to read the Voltage on the cab control.
If the voltage is enought to stop the unint you must see a "+" before the indication of the voltage.
swansea-turkeys
24-10-2010, 06:52 PM
thanks, it says auto on the function menu, what do the others mean though? mop?t range abc? etc
is there a user manual available anywhere?
thanks
Marc
swansea-turkeys
24-10-2010, 06:53 PM
You have to read the Voltage on the cab control.
If the voltage is enought to stop the unint you must see a "+" before the indication of the voltage.
thanks, i'll check this now...
marc
swansea-turkeys
24-10-2010, 09:10 PM
yeap, it has the +
Marc
moggy66
24-10-2010, 11:27 PM
OK so you have it on Start/Stop(black circle with to circles inside) should be displayed on the Cab Command if it is not on there the unit will not shut off, and the unit still does not turn off? Using the "Unit Data Key, what is the water temp? you say the Batt voltage is 14.1v this is good.
swansea-turkeys
25-10-2010, 07:07 PM
OK so you have it on Start/Stop(black circle with to circles inside) should be displayed on the Cab Command if it is not on there the unit will not shut off, and the unit still does not turn off? Using the "Unit Data Key, what is the water temp? you say the Batt voltage is 14.1v this is good.
temp says 36 degrees, thanks for your help everyone, it's driving me maddddd
Marc
moggy66
26-10-2010, 01:07 AM
temp says 36 degrees, thanks for your help everyone, it's driving me maddddd
Marc
Theres your problem...the water temp in not hot enough, either the sensor is faulty or you Engine thermostat is stuck open,i can't remeber the exact figures but a temp of 150F is required
swansea-turkeys
26-10-2010, 08:05 AM
Theres your problem...the water temp in not hot enough, either the sensor is faulty or you Engine thermostat is stuck open,i can't remeber the exact figures but a temp of 150F is required
Brilliant thanks, I have a look today and let you know.
Thanks
Marc
Boss302
27-10-2010, 07:16 PM
Water temp has to be 122°F or greater to allow shutdown.
Boss302
27-10-2010, 07:19 PM
Check on Function change the function Auto Op or Manu OP. It Must be set on " AUTO OP" otherwise the unit starts on S/S but don't stop.
Not true. If it is in S/S it is in S/S regardless of the auto op / man op setting. IF it is in Man op and on continuous run. The unit won't start automaticly, it will have to be started with the manual switch. Don't want to see somebody get hurt. S/S is S/S, it will automaticly start and stop.
moggy66
20-11-2010, 01:12 PM
Love to know if this problem is all sorted out now?