View Full Version : Locked rotors in new sealed unit compressors



kiamaian
18-10-2010, 10:24 PM
A couple of years ago I took the opportunity of buying four brand new sealed unit compressors. (Kirloskar AH5515E 1.2 hp) which were old stock. I used two of the compressors without problems. However, after two years I have installed the other two only to find in each case that they won't start and the rotors are locked.

I have made sure the system was not overcharged and there wasn't any blockages in the piping. I have also made sure the wiring and power to the motors is correct.

I now wish I had bench tested them before installation but I have never had this happen to me before.

I can only assume that the pistons have seized over the years due to corrosion or something else.

If I could get compressors to start they will probably be OK.

Has anyone experienced this problem or have any suggestions.

Brian_UK
18-10-2010, 11:41 PM
Single or three phase?

Tried reversing them anyway?

kiamaian
19-10-2010, 01:09 AM
The compressors are single phase. When you say 'reversing' do you mean the active and neutral wires?

kiamaian
21-10-2010, 09:00 PM
This matter has been resolved.

After studying the wiring diagram I found out that I had incorrectly wired the compressors. I reversed the connections to the common terminal and the run terminal and 'bingo' both compressors started up.

My faith has been restored in the manufacturer of the compressors.:D:D

chemi-cool
21-10-2010, 09:06 PM
My faith has been restored in the manufacturer of the compressors.:D:D

Lucky manufacturer, this one was close.....:)