View Full Version : Refrigeration effect



Isaac Appiah
14-10-2010, 10:38 PM
Hi Guys, are there any additives that can be injected the refrigerant cycle - To improve system refrigeration effect? For ACs and all.

Isaac Appiah
14-10-2010, 10:42 PM
No, I mean an additive that is injected into the refrigerant to improve its cooling effect.

Brian_UK
14-10-2010, 10:51 PM
No, some firms claim miracles but the only thing that should be inside the pipes is oil and refrigerant.

cool runings
14-10-2010, 10:58 PM
Hi Guys, are there any additives that can be injected the refrigerant cycle - To improve system refrigeration effect? For ACs and all.


If there was anything better than the refrigerant then the refrigerant manufacturer would use it as the refrigerant.

The only thing that should be in with the refrigerant is the oil and we tolerate the oil only because it stops the comp from seizing up.

coolrunnings

.

acnerd
15-10-2010, 06:02 PM
Keep the condenser coils clean and clear of obstructions that could impede airflow.
Keep the evaporator clean and ensure good airflow. Keep the filter clean!!!
As long as the refrigerant charge is correct, then she's doing the best she can! :)

sudarsans
31-10-2010, 03:00 PM
The system efficiency can be maintained only by proper maintenance... It cannot be improved by ant external additive...

chemi-cool
31-10-2010, 07:29 PM
If there was anything better than the refrigerant then the refrigerant manufacturer would use it as the refrigerant.

The only thing that should be in with the refrigerant is the oil and we tolerate the oil only because it stops the comp from seizing up.

coolrunnings

.

There was and unfortunately its gone, its name was R-12,R-502 and R-22.
These was real refrigerants.......

jpsmith1cm
31-10-2010, 08:27 PM
There was and unfortunately its gone, its name was R-12,R-502 and R-22.
These was real refrigerants.......


:eek:



Boy, those were the days.....

Carry 3 cans and you were set...

coolstuf
01-11-2010, 12:14 PM
Not by adding anything, but looking more at your process, clean filters, condensers etc. Installing your condenser in the coolest place also helps. For every 1 deg C you lower your condensing temp, you have 3 % more capacity and use 3 % less energy. These changes cost reletively little. After that there are things like subcoolers etc, with higher cost.

doctor freon
08-11-2010, 02:28 PM
I agree, it would be extremely difficult to optimize further a properly designed, installed, and maintained system by adding another fluid. There are products out there that make claims but the data supporting those claims is severly lacking in my opinion.