View Full Version : fujitsu ducted condensation control nightmare



gille
11-10-2010, 01:27 PM
I have 2 units Fujitsu ARY 60 UUAK / AOY 60 UMAYT with same problem - from time to time it goes to high pressure alarm. After a while get high pressure switch shortcircuited. I observed what is going on, and measured pressures. On outdoor unit fans start at low speed, and high speed is switched on at 37 bar. I think high speed should be switched earlier. What is reason for this? Electronics fault, program or sensor.

bigor_2
12-10-2010, 12:14 PM
Hi Gille,

in cooling mode speed of outdoor fan set ambient thermistor. Can be an ambient temperature became low +5C?

gille
15-10-2010, 01:07 PM
You are right, I'll have to check thermistor, but I do not have ohm/temp table, maybe i could try to relocate thermistor.
Thank you.

bigor_2
15-10-2010, 02:02 PM
see http://www.refrigeration-engineer.com/forums/showpost.php?p=206410&postcount=26

Nike123 worked hard for me)